Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Sigma - Communications with the controllers is very slow.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sigma - Communications with the controllers is very slow.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa125819
    sesa125819
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
929 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sigma - Communications with the controllers is very slow.

Picard Product_Support
‎2018-09-06 12:20 PM

Issue

Communications with the controllers is very slow.

Environment

Slow communications

Displaying objects seem to lock up

Globals

V53 hardware

Cause

Communications with the controllers is very slow. Objects will display correctly once, but if the display is carried out several times, or if an object is overridden, the server appears to lockup.

Resolution

The issue was caused by two Sigma objects being globally transmitted at the rate of 12 per second. The two objects were Programmable and the programme had been incorrectly written as follows;

10 IF POINT 0|108 = 0.000000 THEN RETURN "Ch1  Off"
20 IF POINT 0|108 = 1.00000 THEN RETURN "Ch1 Start"
30 IF POINT 0|108 = 2.00000 THEN RETURN "Ch1 Running"
40 IF POINT 0|108 = 3.00000 THEN RETURN "Ch1 Shutdown"
50 IF POINT 0|108 = 4.00000 THEN RETURN "Ch1 Service"

The above object is incorrect because it does not specify True or False.

Because globals are transmitted on "change of state" the global was being transmitted with every scan of the object file.

It is recommended that the object is changed as follows.

10 IF POINT 0|108 = 0.000000 THEN RETURN FALSE "Ch1  Off"
20 IF POINT 0|108 = 1.00000 THEN RETURN TRUE "Ch1 Start"
30 IF POINT 0|108 = 2.00000 THEN RETURN TRUE "Ch1 Running"
40 IF POINT 0|108 = 3.00000 THEN RETURN TRUE "Ch1 Shutdown"
50 IF POINT 0|108 = 4.00000 THEN RETURN TRUE "Ch1 Service"

Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (1)
  • Find more articles tagged with:
  • 7969
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of