Communication with a Sigma controller via its LAN connection is not possible when connected through another controller’s service port.
Satchwell BAS & Sigma
Satchwell Sigma
When the Sigma system is incomplete or lacks access to a Sigma server:
  • Messages generated by controllers cannot be delivered to the server
  • These messages accumulate in the Alarm Buffers
  • This buildup can block communication between controllers
If the system will operate without a Sigma server, apply the following recommendations:
  1. Avoid programming object alarms
  2. Do not configure system logging
  3. Avoid configuring global objects unless full controller access is guaranteed
  4. Create an archive of the controller for backup
  5. If the system will be offline for less than 5 days, use Set Controller Mode:
    • Navigate to:
      System Diagnostics → Options → Set Controller Mode
    • Select the functions to inhibit
    • Set the duration (up to 7200 minutes)