Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Sigma - Analogue input channels do not display the correct value.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sigma - Analogue input channels do not display the correct value.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa125819
    sesa125819
  • RogerHa
    RogerHa
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1012 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sigma - Analogue input channels do not display the correct value.

Picard Product_Support
‎2018-09-06 12:39 PM

Issue

Analogue input channels do not display the correct value.

Environment

Sigma

Analogue Input

AI

Channel

Cause

Analogue Input values do not display the correct value. This issue is not confined to one card, or even one controller.

Resolution

The fact that the problem is spread across several analogue input channels, cards and controllers, suggests that the problem is not due to the specific objects themselves, and that some external influence is having an affect.

Carry out the following checks;

The issue is only seen on one controller.

  • Disconnect all inputs to the card except for one. This should be a resistive input. If this has helped, then investigate the other inputs.
  • Disconnect the wiring to the connected analogue input and replace it with a fixed resistor. The reading should be stable.
  • If this input still reads incorrectly then change the object lookup table entry to 2000, measure the voltage across the resistor and compare it with the maximum input voltage of 2 volts.
  • Example measured voltage of 1.5 volts. - 1.5/2.0 = 0,75 * 100 = 75. AI object should display 75
  • Confirm that the controller earth bar is connected to a good earth.
  • Consider replacing the AI card.
  • Consider replacing the CPU card.

The issue is only seen on one controller, but with multiple analogue input cards.

  • On all of the cards disconnect all of the analogue inputs, except for one input on one card. This should be a resistive input. If this has helped, then investigate the other inputs.
  • Confirm that the controller earth bar is connected to a good earth.
  • Consider replacing the AI card.
  • Consider replacing the CPU card.

The issue is seen on multiple controllers.

  • It is very likely that there is an earth issue, confirm that the controller earth bar is connected to a good earth on all controllers.
  • Older type Power Supply boards (Bas-to-Sigma upgrades) can also cause many different (seemingly unrelated) problems, especially when the voltage
    regulator IC's start to overheat due to the bolt securing the tab of the regulator to the heatsink becoming slightly loose: the regulator IC's go into 'current limit' mode.
    Re-tightening these (and also the bolts securing the TO3 type regulator) and allowing the heatsink to cool-down will often cure problems.

     
Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (1)
  • Find more articles tagged with:
  • 7368
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of