Issue
Alarms generated by Sigma controllers are sometimes delayed in appearing at the Sigma server. This behavior is inconsistent—manual alarm tests display correctly, but real-time alarms may not appear until other activities are performed.
Product Line
Satchwell BAS & SigmaEnvironment
Satchwell Sigma
Cause
There are two recommended solutions depending on your network setup:
Option 1: Disable Windows Firewall
If the Sigma server is not connected to the Internet, you can safely disable the Windows Firewall to allow uninterrupted alarm communication.
⚠️ Note: The method to disable the firewall varies by operating system. Use the system's Help feature for guidance.
Option 2: Add a Firewall Exception
If disabling the firewall is not viable, configure a firewall exception for Sigma:
- Open Windows Firewall.
- Navigate to the Exceptions tab.
- Select Add Port.
- Enter the following details:
- Name: Sigma UDP Port
- Port Number: 49152
- Protocol: UDP
✅ This allows Sigma alarm messages to pass through even when the firewall is active.
Additional Notes
- Port 49152 is specific to Sigma and must be configured as a UDP port.