Issue
Using the 0 - 20 mA output on the new surface mount Analogue Output boards.
Environment
Sigma
X96 Outstations
New style surface mount Analogue Output boards
Cause
Configuration of the Analogue Output board for use where a device requires a 0 - 20 mA control signal.
Resolution
The new style surface mount board provides channels 15 and 16 for use with devices that require a 0 - 20 mA instead of the traditional 0 -10volts.
Channels 15 and 16 can be configured for 0 - 10 volts or 0 - 20 mA by selecting the appropriate setting for link LK1, which is located on the board.