Shrink the SQLite event and trends databases (Option 2) by creating a new file

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Shrink the SQLite event and trends databases (Option 2) by creating a new file
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3616 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Shrink the SQLite event and trends databases (Option 2) by creating a new file

Picard David_Purser Picard
‎2024-02-07 11:20 AM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:32 AM

Issue

In some cases, the event and trend database can grow really big, although not all the space in the files is used. In extreme cases, there is more free space than used space and it is quicker to create a separate file.

Product Line

EcoStruxure Building Operation

Environment

  • SQlite
  • Building Operation Enterprise Server
  • Building Operation Enterprise Central

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Cause

Frequent inserts, updates, and deletes can cause the database file to become fragmented - where data for a single table or index is scattered around the database file. Running VACUUM ensures that each table and index is largely stored contiguously within the database file. In some cases, VACUUM may also reduce the number of partially filled pages in the database, reducing the size of the database file further.

Read further information here: https://www.sqlite.org/lang_vacuum.html

Resolution

  1. Stop the Enterprise Server or Enterprise Central.
  2. Open SQLiteStudio (link to download)
  3. Select "Databases" --> "Add database"
  4. Find the event.db or trend.db file from the "historical" folder of the EBO database folder. Use this article to locate for your installation - Clean db for Enterprise Server or Enterprise Central
  5. On the added database, right-click and select Connect to the database
  6. In the query tab, paste the following command:
    1. VACUUM main INTO 'C:\ProgramData\Schneider Electric EcoStruxure\Building Operation 6.0\Enterprise Server\db\Historical\event2.db';
  7. Update the path to match your installation. One can SHIFT-RIGHT-CLICK the event.db or trend.db and select Copy as Path, then select everything inside the single quotes and paste. The paste will include double quotes, so delete those and leave the single quotes
  8. Update the database name to ensure it is unique.
  9. Click the blue play button above the Query tab.KBVacuumInto.png
  10. Depending on the size and amount of free space, this can take seconds to days to complete. One can monitor the progress in Windows Explorer by seeing the Size and Date Modified field update.
  11. Append .old to the end of the original file and rename the new file, event.db or trend.db, so it replaces the original.
  12. Start the Enterprise Server or Enterprise Central.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • DavidPurser24
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore