Seven Trends not obeying base time 00:00
  • Seven Trends not obeying base time 00:00
  • RobertAndriolo
    RobertAndriolo
‎2018-09-06 10:07 AM
Receive data from Trend log (Seven Trends) with incorrect base time hh:12 even though it is set to 00:00.
I/NET Seven
Seven Trends
Xenta Server 527 / 527-NPR / 731
When using a Xenta Server as an I/NET NetPlus Router (NPR) and have configured a Trend (Seven Trends) with a sample count of 24 and sample interval of 60 minutes it appears that the time is incorrectly reported to the I/NET Host.  This issue will be rectified in a future release of the Xenta Server firmware.
As workaround to this issue, the Sample Count value below 24 should be used.
This is issue is not seen when using a Direct Connect configuration
  • TAC INET
Tags (2)
  • 14160
  • qt8482