Setting up ID Works on a Remote Client PC

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Setting up ID Works on a Remote Client PC
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1856 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Setting up ID Works on a Remote Client PC

Picard Product_Support
‎2018-09-07 11:05 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:59 AM

Issue

Setting up ID Works on a Remote Client PC

Product Line

TAC INET

Environment

  • I/NET Seven
  • ID Works
  • Windows XP
  • Windows 7 32-bit
  • Windows 7 64-bit

Cause

Configuring the I/NET System to be a “Server/Remote Client” format and the ID Works software is going to be on a Remote Client PC.

Resolution

The first procedure is to modify the ODBC Data Source. The steps for this are very dependent upon the PC's operating system. Reference page 2-14 through 2-23 of TCON 301, the chapter named Modifying TAC I/NET Seven's ODBC Data Source. 

Once the ODBC Data Source is configured, proceed with the steps below:

  1. Go into the ID Works Administrator Editor and select the System tab.
  2. Scroll down to the Photo Path option.
  3. Direct the current path to the PC that is going to be the Server.
    In this example, the PCs Name and Photo location is: \\TPServer\CDrive\I7photos


     
  4. Go into the ID Works Designer Editor open each of the site badge templates and modify them for the Server PC link.
    1. Open one of the templates.
    2. Highlight the Image path square and do a right mouse click.
    3. Go to the Field Properties option.
    4. Set the path to the Server PC location for the badge photos. See the example below for further information.


       
  5. In this example the server PC is named TPServer. Badge photos are in the C:\I7photos\Thumbnail directory. There are only eight pictures entered at the time these captures were made. The jpegs for those eight individuals were saved to the folder using the CardNumber as the name shown below:

Labels (1)
Labels:
  • TAC INET
Tags (4)
  • Find more articles tagged with:
  • 5061
  • Datacard
  • ID Works
  • Remote Client
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore