Issue
How to set up a Operator Panel to only see the TAC Xenta controller it is plugged into
Product line
EcoStruxure Building Operation
Environment
TAC Xenta Operator Panel firmware 3.7
TAC Xenta Programmable controller 3.85 or higher
Cause
When the Operator Panel is plugged into a TAC Xenta programmable controller the whole network of TAC Xenta controllers are listed.
Resolution
This option and the requirements are described in this TPA To enable the option in the TAC Xenta: Ho...