Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Setting a TAC Xenta Operator Panel to only view the local Xenta programmable controller

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Setting a TAC Xenta Operator Panel to only view the local Xenta programmable controller
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • PeterEdvik
    PeterEdvik
  • MikaelKrantz
    MikaelKrantz
  • DavidFisher
    DavidFisher
  • Benji
    Benji
  • PeterLarsen
    PeterLarsen
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2097 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Setting a TAC Xenta Operator Panel to only view the local Xenta programmable controller

Picard Product_Support
‎2018-09-11 07:27 AM

Issue

How to set up a Operator Panel to only see the TAC Xenta controller it is plugged into

Product line

EcoStruxure Building Operation

Environment

TAC Xenta Operator Panel firmware 3.7

TAC Xenta Programmable controller 3.85 or higher

Cause

When the Operator Panel is plugged into a TAC Xenta programmable controller the whole network of TAC Xenta controllers are listed.

Resolution

This option and the requirements are described in this TPA


To enable the option in the TAC Xenta:

How to enable this in the TAC Xenta: Edit the application and create a Public PVI-block with the name XENTASYSREG and set this block’s initial value to 8. If you have multiple TAC Xenta OP panels in the network, each one connected to a specific TAC Xenta Controller, it will be required to create this special PVI block in every one of these TAC Xenta Controller’s application code.

 

To enable the option in the OP Panel:

1. Open the TAC Xenta OP local service menu, by pressing and holding the “escape” and “enter” buttons for a few seconds.

2. Enter the bottom command: “11 OP connects to”.

3. Enter this sub-command, and then type in, using “+” or “-“, the specific TAC Xenta controller’s subnet and node address you want this OP to be “locked” to. The TAC Xenta controller subnet and node addresses can easily be found in TAC Vista Workstation; select “properties” for the TAC Xenta controller and the subnet/node address will be displayed.

Observe that when you select, in the OP panel’s new menu, the node number and press enter the TAC Xenta OP will restart and seek for this now selected TAC Xenta controller. Note that it is still possible to access this specific TAC Xenta controller from another TAC Xenta OP in the network if that TAC Xenta OP is of a version prior to 3.70 or this new “lock-function” is not enabled in that TAC Xenta OP. However doing this, you will only here also “see the local TAC Xenta controller”. In this case you will be able to exit this TAC Xenta controller again by pressing “escape”. While in the locked TAC Xenta OP you will not be able to exit from the TAC Xenta controller it is locked to.

Labels (1)
Labels:
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 15953
  • MikaelKrantz19
Was this article helpful? Yes No
0% helpful (0/1)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of