Setting a TAC Xenta Operator Panel to Only View the Local Xenta Programmable Controller

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Setting a TAC Xenta Operator Panel to Only View the Local Xenta Programmable Controller
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • MikaelKrantz
    MikaelKrantz

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2377 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Setting a TAC Xenta Operator Panel to Only View the Local Xenta Programmable Controller

Picard Product_Support
‎2018-09-11 07:27 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-02 04:23 PM

Issue

When a TAC Xenta Operator Panel (OP) is connected to a TAC Xenta programmable controller, it displays the entire network of TAC Xenta controllers. In some cases, it's desirable to restrict the OP to only view the local controller it is directly connected to.

Product line

TAC Vista

Environment

  • TAC Xenta Operator Panel firmware 3.7
  • TAC Xenta Programmable controller 3.85 or higher

Cause

By default, the TAC Xenta OP scans and displays all TAC Xenta controllers on the network. This behavior may not be suitable for installations where each OP should only interact with its directly connected controller.

Resolution

To restrict a TAC Xenta OP to only view its local controller, follow these steps:

1. Configure the TAC Xenta Controller

  • Edit the application in the TAC Xenta controller.
  • Create a Public PVI block named:
    XENTASYSREG
    
  • Set the initial value of this block to:
    8

Note: If multiple OP panels are connected to different TAC Xenta controllers on the same network, you must create this PVI block in each respective controller's application code.


2. Configure the TAC Xenta Operator Panel

  • Access the local service menu on the OP panel:

    • Press and hold the “Escape” and “Enter” buttons simultaneously for a few seconds.
  • Navigate to the command:

    11 OP connects to
    
  • Enter this menu and use the “+” or “–” buttons to select the subnet and node address of the specific TAC Xenta controller to which the OP should be locked.

    • You can find the subnet and node address in TAC Vista Workstation:
      • Right-click the desired TAC Xenta controller.
      • Select Properties to view the address.
  • After selecting the correct node, press Enter.

    • The OP panel will restart and connect exclusively to the selected controller.

Additional Notes

  • If another OP panel (with firmware prior to version 3.70) connects to the same network, it may still access other controllers unless the lock function is also configured on that panel.
  • Once locked, the OP panel will not allow navigation away from the assigned controller.
  • To exit the locked controller view, press “Escape” (only possible if the lock function is not enabled or the firmware is older than 3.70).
Labels (1)
Labels:
  • TAC Vista
Tags (3)
  • Find more articles tagged with:
  • 15953
  • MikaelKrantz19
  • MikaelKrantz25
Was this article helpful? Yes No
0% helpful (0/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore