Sensor Characteristics for Satchwell Controller Type Sensors

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sensor Characteristics for Satchwell Controller Type Sensors
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • Gary
    Gary
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3016 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sensor Characteristics for Satchwell Controller Type Sensors

Picard Product_Support
‎2018-09-10 05:05 AM

Last Updated: Administrator CraigEl Administrator ‎2025-10-26 04:14 PM

Issue

Technicians require accurate resistance values for Satchwell and Sontay sensors to validate performance and troubleshoot temperature-related issues.

Product Line

Field Devices, Satchwell BAS & Sigma, Satchwell MicroNet

Environment

  • Satchwell BAS & Sigma
  • Satchwell MicroNet

Cause

Resistance values vary by sensor type and temperature. Having a reference chart ensures correct diagnostics and sensor replacement.

Resolution

Below is a reference table showing resistance values for various Satchwell and Sontay sensor types across a range of temperatures.

Sensor Resistance Table

DRT, DOT, DDT, DWT, DST, DOS   DD 1401, DW 1202, DR 2253, DWS 1301   DW 1204, DWS 1202   DO 2202
     
Sontay SAT 1   Sontay SAT 2   Sontay SAT 3   Sontay SAT 4
                     
°C Ohms   °C Ohms   °C Ohms   °C Ohms
                     
-40 9711   0 2094   20 2708   -40 2317
-35 9604   1 2079   25 2592   -35 2246
-30 9465   2 2063   30 2474   -30 2163
-25 9288   3 2046   35 2346   -25 2067
-20 9067   4 2027   40 2216   -20 1962
-15 8796   5 2010   45 2086   -15 1849
-10 8472   6 1992   50 1950   -10 1733
-5 8093   7 1973   55 1818   -5 1617
0 7661   8 1953   56 1792   0 1504
5 7182   9 1934   57 1766   5 1397
10 6667   10 1911   58 1741   10 1298
15 6126   11 1892   59 1718   15 1208
20 5573   12 1872   60 1694   20 1128
25 5025   13 1851   61 1669   25 1057
30 4492   14 1830   62 1646   30 996
35 3987   15 1809   63 1622   35 942
40 3518   16 1787   64 1600   40 897
45 3089   17 1764   65 1578      
50 2702   18 1740   66 1553      
55 2358   19 1716   67 1530      
60 2056   20 1690   68 1508      
65 1792   21 1667   69 1484      
70 1563   22 1644   70 1461      
75 1364   23 1621   71 1439      
80 1193   24 1596   72 1417      
85 1047   25 1574   73 1396      
90 921   26 1549   74 1375      
95 815   27 1524   75 1353      
100 722   28 1500   76 1333      
105 643   29 1476   77 1312      
110 575   30 1452   78 1293      
115 517   31 1430   79 1276      
120 466   32 1406   80 1258      
125 423   33 1383   81 1240      
130 386   34 1359   82 1222      
135 353   35 1336   83 1205      
140 324   36 1312   84 1188      
145 300   37 1289   85 1171      
150 278   38 1267   86 1154      
      39 1243   87 1138      
      40 1219   88 1122      
      41 1198   89 1107      
      42 1176   90 1089      
      43 1155   91 1075      
      44 1134   92 1061      
      45 1113   93 1047      
      46 1092   94 1033      
      47 1072   95 1020      
      48 1052   96 1004      
      49 1033   97 991      
      50 1013   98 978      
            99 964      
            100 950      

📎 Note: These values are approximate and may vary slightly depending on installation conditions. Always refer to the official datasheet or use calibrated instruments for precise diagnostics.

Click here to download a pdf with this information.

Labels (3)
Labels:
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
Attachments
Tags (2)
  • Find more articles tagged with:
  • 6803
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore