What are the steps required to send  BACnet Alarms from SmartStruxure Servers to Continuum CyberStation
1. Manually create the CyberStation in  /SBOServer/BACnet Interface/IP Network (upload if required)
2. Create an Alarm/ BACnet Notification within the BACnet Interface Application (make one of the recipients the CyberStation)
3. Point any alarms that are required to be sent to the CyberStation to this Notification
4. In the Continuum CyberStation "Find New BACnet Devices", then send the SBOServer to the database.