Values are displayed in scientific notation (form) when using the folders view.
Vista 4 and Vista 5
When Vista needs to display a number larger than 10,000,000 it converts it to scientific notation (or also known as exponential notation).  So the number of character that need to be displayed are less it displays the number in the following format: 10e6.
This is a normal operation of Vista for large values.
The best solution is to reduce the size of the number. For example go from kilowatts to megawatts.
You can do this by binding the SNVT into a Xenta controller and do a conversion in the controller.  If in a classic lonworks network, you can use an object transfer to bring the SNVT into Menta.