Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Schematic for the RS-232 cable used to direct download Menta applications and system files

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Schematic for the RS-232 cable used to direct download Menta applications and system files
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • CraigEl
    CraigEl
  • Sacco
    Sacco
  • Zhenting_HU
    Zhenting_HU

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4165 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Schematic for the RS-232 cable used to direct download Menta applications and system files

Picard Product_Support
‎2018-09-11 09:09 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 06:17 PM

Issue

Making a cable / adapter by using the cable guide as a reference can be confusing.

Product Line

TAC Vista

Environment

  • Vista
  • Menta
  • Download Wizard

Cause

Without knowing to use a Ribbon (Rollover) Cable, or the correct pins of RJ45 and DB9, it can be difficult to build this cable and adaptor.

Resolution

Note: Pay particular attention to the pins numbers, this view is the inside of the adapter!
This is the pinout to be used in conjunction with a "ribbon" type cable. A Ribbon (Rollover) Cable has inverse ends. For example, Pin 1 of one RJ45 will be Pin 8 at the other end, Pin 2 will be 7, Pin 3 will be 6 and etc..

                            

 

 

Here is a Diagram which highlights the path of TxD RxD and GND from the PC to the Xenta Controller. Use and Ohm meter to check the continuity of connections.

If you are having communication problems, please see Verifying Serial Port Communications with loopback test   for further troubleshooting tips.               

Alternatively, a cut ethernet cable can be wired to a DB9. DO NOT use an Ethernet Cable with the above adapter.

1. Use a standard 586B RJ45 ethernet cable pictured below.

              

2. Connect RJ45 jack to a DB9F according to the following diagram.

Labels (1)
Labels:
  • TAC Vista
Tags (3)
  • Find more articles tagged with:
  • 11787
  • kabelguide
  • kableguide
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of