Schedule in the AS will not control value in a b3 controller
  • Schedule in the AS will not control value in a b3 controller
  • Dave_Shore
    Dave_Shore
  • DavidChild
    DavidChild
  • JohnBoehmer
    JohnBoehmer
‎2018-09-06 10:13 AM
Last Updated: Sisko DavidChild Sisko ‎2020-02-24 02:49 AM
An Enumerated schedule created under the BACnet Interface application folder will not control a digital value (Occupancy) in a b3 controller.
Other b3 controllers are handling this with no trouble.
  • b3
  • Variable Connectors(variable connectors were replaced in v1.5)
  • Schedules
  • bindings
Broken variable connectors.
  • Delete the bindings and perform a Repair References on variable connectors.
  • The digital value responded properly once the schedule binding was re-established.
NOTE Variable connectors were replaced in SBO 1.5 and therefore this article in not relevant to the current product