Issue
An Enumerated schedule created under the BACnet Interface application folder will not control a digital value (Occupancy) in a b3 controller.
Other b3 controllers are handling this with no trouble.
Product Line
EcoStruxure Building Operation
Environment
- b3
- Variable Connectors(variable connectors were replaced in v1.5)
- Schedules
- bindings
Cause
Broken variable connectors.
Resolution
- Delete the bindings and perform a Repair References on variable connectors.
- The digital value responded properly once the schedule binding was re-established.
NOTE Variable connectors were replaced in SBO 1.5 and therefore this article in not relevant to the current product