Satchwell MB / MBX valve range - Reconditioning the valve using the 617-9-4xx kit.
  • Satchwell MB / MBX valve range - Reconditioning the valve using the 617-9-4xx kit.
  • sesa125819
    sesa125819
‎2018-09-10 07:34 AM
Reconditioning  a Satchwell MB/MBX valve using the 617-9-4xx kit.
Satchwell
MB
MBX
Reconditioning
Valve
Drawings of the valve internal assembly were not available.
The reconditioning of an MB / MBX value is not easily undertaken, and it is recommended that the valve is removed from the pipework to carry out this process.
If removal from the pipework is not possible, then it is essential that the system water is completely isolated from the valve, and that any remaining water in the valve is drained away.
Please note; that if the valve is not isolated correctly, then when the valve front is removed, it will be virtually impossible to reassemble it, and should the water be hot, then serious injury might occur.
To refer to the valve internal assembly, please click HERE. It should be noted that the illustration relates to those MB Valve Bodies having 2 shoes (1.1/2”&2” only), the smaller valves only have one shoe.
To refer to the "Recondition Kit Drawing", please click HERE.
To refer to the "O ring Assembly", please click HERE.
  • Field Devices