SP-MNR2: How to factory default the module
  • SP-MNR2: How to factory default the module
Lieutenant JG JamesMorgan Lieutenant JG
‎2023-12-14 12:34 PM
Last Updated: Crewman ContentModerator ‎2025-09-01 03:32 AM
If you lose access to your comms expander or need to reset all of the settings how do you default the module?
Security Expert Expert
Security Expert SP-MNR2 Firmware 1.0.27 (and higher)
Warning
Hazard of Electric Shock: Remove all power from all devices before removing any covers or doors of the system. Disconnect power at the device and at the power source.
Electrostatic Discharge Required: Always discharge static electricity from your person by touching metal prior to handling any hardware. Failure to do so may result in damage to devices.
A physical link is needed to default the module
These are the settings that are resets
  • Password to admin
  • Repeater Mode to RS-485 mode
  • UDP IP/Host to 192.168.1.2
1. Link the N+ N- NA and NB connections between all three COM ports
2. Cycle power to the device
Please note: this does not reset the IP address, so you may need to default the IP address separately.
1. Unlink all COM3 terminals and leave COM 1 and 2 linked
2. Cycle power and connect to the built-in web interface at 192.168.111.222
3. Configure IP address as desired