SHR100-T temperature sensor fluctuating
  • SHR100-T temperature sensor fluctuating
  • PeterLarsen
    PeterLarsen
‎2018-09-06 01:30 PM
When a SHR100-T is setup with a 0-10 volt humidity sensor the temperature reading fluctuates
Xenta controllers
I/NET Controllers
SHR100-T Temperature Humidity Sensor
Interference from the 24Volt AC power supply in the same cable causes this temperature fluctuation.
 The two tested fixes that stabilize the temperature reading are.
  1. Set the humidity as a 4-20mA signal, this will stabilize the temperature reading.
  2. Run the 24Volt AC power supply in a separate cable. This is the better option if this is noted before installation is started.
Labels (2)
  • TAC INET
  • 5758