SE7xxx Room controller will not come online in BACnet

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • SE7xxx Room controller will not come online in BACnet
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2611 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

SE7xxx Room controller will not come online in BACnet

Picard Product_Support
‎2018-09-06 10:51 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:57 AM

Issue

Cannot see a SE7300 Room Controller when connected to a BACnet MS/TP network.

Product Line

Andover Continuum, EcoStruxure Building Expert, EcoStruxure Building Operation, Field Devices

Environment

  • SE7000 Series
  • SE7000, SE7200, SE7300, SE7600, SE76x7
  • Ex Viconics branding VT7000 Series
  • Viconics room stats with BACnet communications

Cause

Units are shipped from the factory with the BACnet network disabled.

Resolution

  1. Power up the unit.
  2. Press the middle button down for 8 Seconds (It is either the Override or °C/°F Button depending on model).
  3. Enter the password if it has been set, or leave as the default 0 for no password (as shipped from the factory).
  4. Use the down key to find the "Comm Addr" value.
  5. By default this is set to 254 BACnet communications disabled.
  6. Adjust this to the desired value within the valid range of 1 to 127, but also ensure it is in the range of your BACnet Max Master setting on the connected system.
  7. Once set, power off/ on the unit to change the address to the new value.
  8. The unit should now be visible on the BACnet MS/TP network. 

 

Note:

  • The SE7xxx Room controllers will auto baud to match your MS/TP network, there is no baud rate setting to adjust.
  • Also any password set on the SE7xxx controller must be temporarily disabled to allow the middle button to operate correctly.
  • For further information on installing the Room Controllers please see SE7000 Series Installation Instructions.
Labels (4)
Labels:
  • Andover Continuum
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • Field Devices
Tags (5)
  • Find more articles tagged with:
  • 12099
  • device
  • devices.
  • discover
  • mstp
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore