Issue
SDCU or Pocket Terminal fails to operate when connected to the service port of certain Sigma Controllers.
Product Line
Satchwell BAS & SigmaEnvironment
- Sigma Controllers (UNCx96, UNC632, DNN, IC3)
- SDCU (Sigma Device Configuration Utility)
- Pocket Terminal
Cause
The issue may arise due to the PL* pluggable connector being occupied. This connector might be:
- In use by a SigmaCE device
- Connected to a serial device (e.g., Bluetooth)
- Pre-wired to another component
Resolution
-
Identify the connector in use:
- UNCx96 → PL4
- UNC632 → PL5
- DNN / IC3 → PL5
-
Action Steps:
- Check if the PL* connector is currently in use.
- If so, unplug the connector.
- Reconnect the SDCU or Pocket Terminal and test functionality.