SCU Second Station not working properly
  • SCU Second Station not working properly
  • Roger_Bently
    Roger_Bently
‎2018-09-06 02:46 PM
SCU in double-address mode and the second station is not responding.
Once a card is read at any of the readers, a Reader Entry is displayed in the Transactions Window but the strike never fires.
The DO point can be manually controlled through Software but not by any of the readers.
  • I/NET
  • SCU1284
The MCU Configuration must be set to restore the DPU.
  1. Connect to the controller, then go to MCU Configuration.
  2. Both of the addresses on the DPU should be Blue.
  3. Turn the second address to Internal and exit the editor.
  4. Open the Editor again and change the setting to DPU.
  5. Perform a DPU restore and try the card again.
  6. A Reader Entry should show up in the Transactions Window and the strike should fire, indicating that it is working properly.
  • TAC INET
  • 3102