Running reports on Extended Logs shows no data

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Running reports on Extended Logs shows no data
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa119747
    sesa119747
  • Alan_Wood
    Alan_Wood
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2038 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Running reports on Extended Logs shows no data

Picard Product_Support
‎2018-09-06 02:42 PM

Issue

Running reports on Extended Logs shows no data

Environment

Continuum system

Cause

Possible Causes:

  • Other programs currently running extended logging (pre-1.7x style).
  • Time sync errors
  • Cyberstation preference is set to false

Resolution

  1. Check that you do not have programs running that are performing extended logging the pre-1.7x style. Any programs that were used for extended logging should be disabled or removed.
  2. Check the Continuum Error Log listview and see if there are time sync errors. A difference of more than 5 minutes between the Master controller and the Cyberstation will stop extended logging from working properly. You will see an error indicating that the time difference has been exceeded.
  3. Ensure the Cyberstation preference is set to True
    Download Extended Log Data from Controllers on the LAN(RAS)
    If it was set to false, Stop/Restart Continuum

Run List views of all points, (inputs, outputs, numerics)
Example:

  1. In Explorer, Go to ListView> Listview_Infinity Inputs > Edit
  2. Click Columns> Add a Column
  3. Add ExtLogEnable
  4. Check Off Edit box
  5. Click Apply then the General Tab
  6. Run the listview
  7. Select Edit> Select All
  8. Select Object> Set Attributes
  9. Select ExtLogEnable, For Value type in True and Click OK, OK
  10. Select View> Refresh list and the attributes are set to true
  11. Repeat this for Outputs and Numerics
  12. Wait for awhile beyond how often you are logging your points.
  13. Run reports to verify data is being logged.

NOTE: Occasionally, after an upgrade, you may need to set all the extended log enable attributes to FALSE FIRST and then to true again for inputs, outputs and numerics to get them working.

Data may have been logging and then stopped. The data range requested in the report doesn’t have data, but there is data in the database. Here are some tips on verifying the data in the database.

Using Enterprise Manager

  1. Use Query Analyzer against the Continuumdb
  2. Select * from extendedlog

Using OSQL

  1. Go to a command prompt
  2. Enter in osql –Uandover97 –Ppyramid97 –S then enter (this assumes default user and pw, change if needed. –S needs to be followed by your server name Once you hit enter you’ll be brought to the 1> prompt
  3. At the 1> Prompt hit the Enter key
  4. 1> select * from ExtendedLog
  5. Type Go the Enter
  6. If values are returned, then extended logging is working.
  7. Type quit (to exit OSQL)
  8. Type Exit to close the DOS window
Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 3234
Was this article helpful? Yes No
0% helpful (0/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore