Running I/NET Seven with a "User" group

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Running I/NET Seven with a "User" group
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • Tom_Poovey
    Tom_Poovey
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1665 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Running I/NET Seven with a "User" group

Picard Product_Support
‎2018-09-10 08:55 AM

Last Updated: Picard RobertAndriolo Picard ‎2021-03-02 10:02 PM

Issue

  • How to run I/NET Seven Software as a local user
  • Customer does not WIndows User logged in with Local Administrator rights to run I/NET Seven Software 

Product Line

TAC INET

Environment

  • Windows 7
  • Windows 10
  • I/NET Seven Rev 2.41 and above 

Cause

The IT department requires that I/NET Seven runs using a Windows "User Group" instead of the usual "Local Admin"

Resolution

 

Define the Windows User Account

  1. Temporarily log into the PC with the desired User account using “Local Admin/Administrator” rights.
  2. Turn off the “User Account Control: (UAC) following the directions defined in this article Windows 7/10 User Account Control Settings 
    If this is not done then every time you try to enter an I/Net editor, using the “User” Group you will be asked to login as a “Local Admin”
  3. Change the User account back to the "User" Group

I/NET Seven Feature Matrix:

Review the following table showing all the editors both the “Local Administrator” and the “User” can access with their “Windows” Rights.

  • Note: **The I/Net Editor “DbCreate Functions”. If you log into "DbCreate with the "SQL Server Authentication" then these items will be "Y". If you do not give the "Windows User" the SQL Username and Password then these items will be "NO"
  User Account
I/NET Seven Operation Administrator  User
Install I/NET Y NO
Remove I/NET Y NO
Upgrade I/NET Y NO
I/NET Configuration Y Y
     
DBCreate Functions    
Create db Y Y **
Import I/Net 2X Y Y **
Verify existing db Y Y **
Remove existing db Y Y **
Backup db Y Y **
Restore db Y Y **
Import Docutrend Archive Y Y **
Upgrade db Y Y **
     
Seven Reports    
View Y Y
Run Y Y
Configure Y Y
Save Y Y
Print Report Y Y
Mount Archive Y Y
View Archive Y Y
Run Archive  Y Y
Print Archive Report Y Y
     
Archive Configuration    
Event Archive Configuration Y Y
Run Y Y
Trend Archive Configuration Y Y
Run Y Y
View  Y Y
     
I/O Server Configuration    
Promote Filemaster Y NO
Demote Filemaster Y NO
Promote Client Y NO
Demote Client Y NO

 

Labels (1)
Labels:
  • TAC INET
Tags (4)
  • Find more articles tagged with:
  • 7494
  • groups
  • inet
  • RobertAndriolo21
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore