Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Requirements for the MNB-1000 to communicate properly via BACnet Ethernet

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Requirements for the MNB-1000 to communicate properly via BACnet Ethernet
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • sesa119747
    sesa119747
  • sesa116871
    sesa116871
  • Julio_Cortes
    Julio_Cortes
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2786 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Requirements for the MNB-1000 to communicate properly via BACnet Ethernet

Picard Product_Support
‎2018-09-06 02:43 PM

Last Updated: Guinan RandyDavis Guinan ‎2023-08-16 06:52 AM

Issue

A correct IP, Subnet Mask, and Default Gateway addresses are required for the MNB-1000 to communicate properly via BACnet/IP but what about BACnet Ethernet?

BACnet IP requires a valid IP address to be routed in a TCP/IP network. please read the example below in the resolution

BACnet Ethernet requires a valid six-byte MAC address assigned by the manufacturer and only operates within layer 2 of the OSI model.  It is non-routable protocol

Example of Ethernet address:  00:00:AC:56:78:90

Product Line

TAC IA Series

Environment

I/A Series MNB 1000

Cause

BACnet IP is a requirement and needs information on configuring the settings to enable communications.

Resolution

MNB-1000 controllers must have a valid IP address, Subnet Mask address, and Default Gateway address for the communication ports to function properly if BACnet/IP is enabled. If 0.0.0.0 is used, the communications ports may be disabled and no longer communicate after the controller is reset. In the event that 0.0.0.0 was entered and the communications port is disabled, there is currently no field workaround or way to repair it. The controllers will have to be returned to the factory for repair. Never enter an invalid IP, Subnet Mask, and Default Gateway address for new installations. Review and update current installations. To connect to the MNB-1000 for the first time it will require an Ethernet connection.  When you select the BACnet IP tab and enable IP the default IP address from the factory is a valid address of 10.1.10.2 with a subnet mask of 255.255.255.0. Default example:

  1. IP address 10.1.10.2
  2. Subnet mask 255.255.255.0
  3. Gateway 0.0.0.0  (If you do not have a default gateway IP address then enter 0.0.0.0 in the default gateway section)
Labels (1)
Labels:
  • TAC IA Series
Tags (2)
  • Find more articles tagged with:
  • 3201
  • RandyDavis23
Was this article helpful? Yes No
0% helpful (0/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore