Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Requirements for connecting Pelco's Endura to TAC I/NET Seven

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Requirements for connecting Pelco's Endura to TAC I/NET Seven
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • sesa139513
    sesa139513
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3475 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Requirements for connecting Pelco's Endura to TAC I/NET Seven

Picard Product_Support
‎2018-09-07 07:40 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 06:52 PM

Issue

The Pelco Endura system with cameras at a location and integrating with the TAC I/NET Seven system.

Product Line

TAC INET

Environment

Check the system requirements for the version of TAC I/NET Seven and Pelco Endura 

Cause

Configuration requirements of the Pelco Endura and TAC I/NET Seven are specific for the functionality in I/NET.

Resolution

Once your Pelco Endura system is configured and the Workstation has discovered all the devices and the System Manager is online with the cameras correctly configured, there are four basic requirements to connect TAC I/NET.

  1. Cameras have to have a unique friendly name other than default.
  2. Cameras have to have a unique camera number.
  3. Netframework 3.5 has to be installed.
  4. Windows Media Player 11 has to be installed.

 

If using I/NET Seven Release 2.40a then the following applies:
Once INET and the requirements above are installed the Endura Install can be run.
The installer for these files is located on the INET CD in the folder: Support\EnduraSDK.
Note: Endura video does NOT work on Windows Vista or Windows 7.
 
If using I/NET Seven Release 2.40 or above:
Dual NIC support is now available. For Endura, 100GB NIC and Router are suggested. 1 for I/O Server, 1  for video
 
Equipment used:
  • NSMS200 Pelco Endura Network System Manager & Network Video Manager
  • SM5000 Pelco Endura System Manager
  • WS5070 Pelco Endura Workstation with Advanced Management Software
  • WS5000 Pelco Endura Work Station Software package
  • NET5301T Pelco Endura Video Encoder
  • Spectra IV Pelco Camera

Visit Pelco.com for more information.

Click here to view an extended compatibility matrix for Endura and I/NET.

Labels (2)
Labels:
  • CCTV
  • TAC INET
Attachments
Tags (1)
  • Find more articles tagged with:
  • 4113
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of