Report or Extended Trend Log not showing the most recent data

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Report or Extended Trend Log not showing the most recent data
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Dave_Shore
    Dave_Shore
  • DavidChild
    DavidChild
  • Derrick_Ratliff
    Derrick_Ratliff
  • RobertAndriolo
    RobertAndriolo
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
2854 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Report or Extended Trend Log not showing the most recent data

Picard Product_Support
‎2018-09-06 09:44 AM

Last Updated: Dave_Shore Schneider Alumni (Retired) ‎2019-09-13 07:17 AM

Issue

Report or Extended Trend Log not showing the most recent data

Product Line

EcoStruxure Building Operation

Environment

  • Interval Trend Logs
  • Extended Trend Logs

Cause

The extended trend log will only pull information from the Trend log when the Threshold is reached.

Resolution

OPTION 1 - Use the maximum Transfer Interval property.

  • Edit the Extended Trend Log
  • Change the Maximum Transfer Interval property from "Disabled" to the maximum time you want to go between updates in the extended trend log.

NOTE: You should not set every extended trend log to 1 minute as this will cause unneeded strain to the system. If you need current data, look at the Trend Log. Use Extended Trend Logs and Reports for Historic information.

OPTION 2 - Use the Transfer trigger variable

  • Create a Digital Value on the Enterprise Server. This can be controlled by a program or a schedule to force the Extended trend log to update before reports are run
  • Edit the Extended Trend Log
  • Set a the Transfer trigger variable as the Digital Value created above.

There are many options with Extended Trend Logs, see System Reference Guide chapter 40.

Additional Notes
1. Extra care should be taken when configuring B3 and Infinet Extended Trend Logs - See Technical Reference Guide for full details.
"You configure extended trend logs differently in Infinet (and b3) devices than you
configure extended trend logs in other EcoStruxure Building Operation devices.
For example, you bind the Monitored trend log property to the Infinet device (and b3)
point or value configured for trend logging. Also, the Threshold property is not
relevant when monitoring extended trend logs regardless of the value you
specify. Finally, you cannot use smart logs when configuring extended trend
logs in Infinet devices (and b3).
Instead of using smart logs, you use the Maximum transfer interval property to
specify the transfer interval." (Technical Reference)
2. To debug logging issues the Force transfer is very helpful, Force transfer Executed by the user to manually force a transfer even though transfer threshold is not reached. (Right click on the Extended Trend Log/Activation/Force Transfer)

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • 15442
  • DavidShore19
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.