Replacing an SP-C or Web controllers - Expanders or Readers

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Replacing an SP-C or Web controllers - Expanders or Readers
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
923 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Replacing an SP-C or Web controllers - Expanders or Readers

Admiral Alan_Wood Admiral
‎2025-01-22 09:06 AM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:31 AM

Issue

For hardware failure or persistent issues, it is necessary to replace Security Expert hardware components

Product Line

EcoStruxure Security Expert

Environment

  • Security Expert
  • SP-C or SP-C-Web controller
  • Expanders (i.e. RDM2 or SP08)
  • Card Readers

Warning

Hazard of Electric Shock: Remove all power from all devices before removing any covers or doors of the system. Disconnect power at the device and at the power source.

Electrostatic Discharge Required: Always discharge static electricity from your person by touching metal prior to handling any hardware. Failure to do so may result in damage to devices.

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Cause

A hardware failure occurs or a persistent issue happens that requires steps to replace Security Expert hardware

Resolution

At times it's necessary to replace Security Expert hardware

 

Steps to replace Security Expert SP-C Controllers:
1. Determine if the original controller has encryption turned on
If the failed controller was setup for encrypted communications with the Security Expert server, the newly installed replacement controller will not have the encryption keys to be able to decode the packets from the server. Attempting to bring it online will be unsuccessful.

On the controller's Configuration tab press the Disable controller encryption, then Yes to confirm.
EncyptionEnabled.png

A replacement controller will typically be unencrypted. As soon as it shows online you can decide if you want to encrypt it. If it was already encrypted in Security Expert before replacing it, you might need to hit the encryption button again to get it in sync.
Note: It can be helpful to use the event server diagnostic. If you see messages including “unencrypted” set encryption on the controller and see if it comes online.
2. Disconnect the old controller from its networks
unplug ethernet and RS-485 module network and other hardware
3. Replace the Serial Number in Security Expert
In Security Expert, navigate to Sites | Controllers. Replace the Serial number of the old controller with that of the new one.
4. Disable encryption
In the Configuration tab, click Disable controller encryption.
5. Default the Controller
If the controller has been used on a different server, default the new controller.
See the SP-C Installation manual for detailed steps on performing a controller default
https://ecoxpert.se.com/search?documentUUID=b4fb1237-fd07-2ee5-d9ad-4324178c364c&title=SP-C%20Securi... 
6. Enter the event server settings on the controller
Log in to the new controller's web interface. In Settings, enter the same IP settings, event server and ports as those of the old controller, then restart the controller.
Note: Remember to remove the jumper used to default the controller
7. Connect the new controller to the networks and hardware
The controller should come online in Security Expert if all the network settings, serial number and encryption settings are in sync.
8. Download the controller

In Security Expert, right click on the controller record and select Force download. The controller should receive the download.
9. Enable encryption
Once the controller is online, in the Configuration tab click Enable controller encryption in Security Expert if desired.


Steps to replace Security Expert SP-C-Web Controllers:

1. Take a backup of the old SP-C Web controller
Login to SP-C Web, In System | Backup controller
This creates a .bak file prompting to save in a folder or in the downloads folder
2. Disconnect the old controller
Unplug the controller from the ethernet network, the RS-485 module network and other hardware.
3. Register the new controller
Log in to the new controller and register it in System | Licensing
4. Restore the previous backup taken
Navigate to System | Backup and Choose File and browse to the previously created .bak file
5. Configure the IP settings
In System | Settings, enter the same IP settings as those of the old controller, then restart the controller
6. Connect the new controller to the networks and hardware and Test

Steps to replace Security Expert Expanders:
1. Disconnect the old 
expander from the RS-485 module network and any inputs, outputs or card readers.
2. Connect the new 
expander to the module network and hardware.
3. Set the new expander's address 
to the same as that of the old expander. 
In Security Expert, navigate to Sites | Controllers, right-click the controller and select Module addressing. 
In SP-C-WEB, use the Expanders Wizard.
To address a keypad, power cycle it and then press [X], [Enter]. Enter the new address and press [Enter] to save.
Note: Sometimes the old expander can remain in the module addressing window even after being physically disconnected. To free up the address, module update the expander record. This will fail, but the address should become available.
4. Module update the new expander. 
The expander should start operating normally using the programming from the original expander.

Steps to replace Security Expert Card Readers:

1. Disconnect the old card reader from the reader port.
2. Connect the new card reader
3. Apply any Custom Configurations
If the reader needs any custom configuration, apply it within two minutes of the reader starting up using the config card.
4. Wiegand and RS-485 readers should connect automatically
For OSDP readers, put the card reader into installation mode, then send an OSDP install mode command to the reader expander.

 

Additional configuration after controllers have been replaced

  • If used at the site, areas that are configured for duress alarms default to un-armed after a SP-C has been replaced and need to be re-armed via forced arming.
  • If used at the site, the alarm dialer (Contact ID) "Service Mode" defaults to "0 - Manual Mode" after a SP-C has been replaced (see the arrow below) and needs to be changed to "1 - Start with controller OS".Service modeService modeService mode


Test the replaced hardware to ensure the issue is resolved



Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (1)
  • Find more articles tagged with:
  • AlanWood25
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore