Issue
How can a faulty IC-LON or IC3-LON be replaced in LonMaker for Windows without requiring new bindings or additional LNS credits?
Product Line
Satchwell BAS & SigmaEnvironment
- LonMaker
- Sigma IC-LON
- Sigma IC3-LON
Cause
When replacing a faulty IC-LON or IC3-LON, the new hardware will have a different Neuron ID than the original device. This typically raises concerns about re-binding and LNS credit usage.
Resolution
LonMaker for Windows includes a Replace Device feature that allows you to substitute a device without affecting existing bindings or consuming additional LNS credits.
Replacement Procedure
-
Install the Replacement IC3-LON
- Use SDCU to configure the new IC3-LON on the Sigma network.
-
Coldstart the Device
- The IC3-LON should automatically coldstart and retrieve necessary files from the Sigma server.
- If it doesn’t, manually initiate a coldstart.
-
Open the LonMaker Project
- Launch the LM4W project used to engineer and commission the original IC-LON.
-
Select the Device in the Drawing
- Right-click the IC-LON device (not the function block) and choose “Replace…”.
- Right-click the IC-LON device (not the function block) and choose “Replace…”.
-
Run the Replace Device Wizard
- Select “Use existing template” and click Next.
- Leave the next screen unchanged and click Next.
- Set the initial state to “Online” and choose “New device values” for Configuration Properties. Click Next.
- Choose your preferred method for entering the new service pin and click Finish.
- Select “Use existing template” and click Next.
-
Commission the New Device
- When prompted, press the Service Pin on the IC3-LON LonWorks daughter card.
- The device will be commissioned and all bindings reasserted.
- When prompted, press the Service Pin on the IC3-LON LonWorks daughter card.
-
Upload Configuration to Sigma Server
- Ensure the NvConfig.bin file is uploaded to the Sigma Server.
- This step is critical to retain binding information after future cold starts.