Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Replacing a faulty Sigma IC-LON in Lonmaker for Windows.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Replacing a faulty Sigma IC-LON in Lonmaker for Windows.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1104 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Replacing a faulty Sigma IC-LON in Lonmaker for Windows.

Picard Product_Support
‎2018-09-11 04:38 AM

Issue

How can an IC-LON be replaced, does it require new bindings to be established in LonMaker for Windows?

Environment

LonMaker

IC-LON

IC3-LON

Sigma

Cause

Faulty IC-LON or IC3-LON hardware is being replaced, the new hardware has a different neuron ID than the original.

Resolution

Lonmaker for Windows (LM4W) has a facility to replace an existing device without affecting existing bindings or requiring additional LNS credits, this procedure will be used to replace the IC-LON.

1. Install the replacement IC3-LON and configure it on the Sigma network using SDCU.

2. The new IC3-LON should coldstart and receive the required files from the Sigma server, if not initiate a coldstart to ensure it has the required files.

3. Connect to the LON and open the LM4W project used to engineer and commission the original IC-LON.

4. Open the LM4W project and select the IC-LON device (Note: select the device not it's function block) in the drawing and choose “Replace…” from the right click menu.

 


 

5. The Replace Device wizard will run.

6. Select use existing template. and click Next.

7. The next screen can be left as is, click Next.

8. Specify “Online” as the initial state as appropriate and select “new device values” as the source of Configuration Properties then click Next.

9. Select the desired method of entering the new service pin then click Finish.

10. The Service pin dialog will be displayed

11. Press the service pin on the IC3-LON LonWorks daughter card and the device should be commissioned and all bindings reasserted.

12. After the replace process is completed ensure that the NvConfig.bin file is uploaded to the Sigma Server so that binding information is retained after a coldstart.

Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (1)
  • Find more articles tagged with:
  • 13994
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of