Replacing a faulty Sigma IC-LON in Lonmaker for Windows.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Replacing a faulty Sigma IC-LON in Lonmaker for Windows.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1249 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Replacing a faulty Sigma IC-LON in Lonmaker for Windows.

Picard Product_Support
‎2018-09-11 04:38 AM

Last Updated: Administrator CraigEl Administrator ‎2025-10-20 05:58 PM

Issue

How can a faulty IC-LON or IC3-LON be replaced in LonMaker for Windows without requiring new bindings or additional LNS credits?

Product Line

Satchwell BAS & Sigma

Environment

  • LonMaker
  • Sigma IC-LON
  • Sigma IC3-LON

Cause

When replacing a faulty IC-LON or IC3-LON, the new hardware will have a different Neuron ID than the original device. This typically raises concerns about re-binding and LNS credit usage.

Resolution

LonMaker for Windows includes a Replace Device feature that allows you to substitute a device without affecting existing bindings or consuming additional LNS credits.

Replacement Procedure

  1. Install the Replacement IC3-LON

    • Use SDCU to configure the new IC3-LON on the Sigma network.
  2. Coldstart the Device

    • The IC3-LON should automatically coldstart and retrieve necessary files from the Sigma server.
    • If it doesn’t, manually initiate a coldstart.
  3. Open the LonMaker Project

    • Launch the LM4W project used to engineer and commission the original IC-LON.
  4. Select the Device in the Drawing

    • Right-click the IC-LON device (not the function block) and choose “Replace…”.
  5. Run the Replace Device Wizard

    • Select “Use existing template” and click Next.
    • Leave the next screen unchanged and click Next.
    • Set the initial state to “Online” and choose “New device values” for Configuration Properties. Click Next.
    • Choose your preferred method for entering the new service pin and click Finish.
  6. Commission the New Device

    • When prompted, press the Service Pin on the IC3-LON LonWorks daughter card.
    • The device will be commissioned and all bindings reasserted.
  7. Upload Configuration to Sigma Server

    • Ensure the NvConfig.bin file is uploaded to the Sigma Server.
    • This step is critical to retain binding information after future cold starts.
Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (2)
  • Find more articles tagged with:
  • 13994
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore