Replacing a 7798 I/Site Controller
  • Replacing a 7798 I/Site Controller
  • Roger_Bently
    Roger_Bently
‎2018-09-06 12:46 PM
How to replace a 7798 I/Site on an existing system without causing any problems to the existing controllers.
All versions of I/Net and 7798B I/Site.
Not doing it properly could cause the system to go down and create problems later on that may or may not be recoverable.
To properly replace a 7798 I/Site the following steps should be performed to ensure minimal downtime and the system is operational again.
  1. Perform a backup of the software and database of the controller.
  2. Remove power, unplug the wires for the C-Lan and Sublan.
  3. Change the controller and turn on the device but do not plug the Sublan plug back in.
  4. Make the necessary changes like address and baud rate etc to match the existing system.
  5. Once communications has been verified, download the bin file and database back to the controller and then plug the Sublan in again.
  6. Go to Edit/Host Computer/Network Configuration and penetrate the link summary that the controller is under and verify that all the devices are communicating and online again.
  • TAC INET
  • 7161