Replacing Xenta 400 series I/O Modules With Xenta 400A series I/O Modules

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Replacing Xenta 400 series I/O Modules With Xenta 400A series I/O Modules
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • Jeff
    Jeff
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2958 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Replacing Xenta 400 series I/O Modules With Xenta 400A series I/O Modules

Picard Product_Support
‎2018-09-07 01:43 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 07:33 PM

Issue

Replacing an older style 400 I/O with 400A series hardware, the Digital Inputs need changed to reflect the newer style of Universal Input.

Product Line

TAC Vista

Environment

  • Xenta 400 I/O
  • Xenta 421, 422, 451, 452
  • Xenta 421A, 422A, 451A, 452A
  • LonMaker Replace

Cause

Hardware changes in the Xenta 400 "A" series I/O will not function as a replacement to a non-"A" series without additional changes to Menta and LonMaker.

Resolution

Part 1- Changes needed within Menta

  1. Open the controller’s application (a Menta file). For ES projects, this file should be stored within C:\TAC\Vista\Applications.
  2. Note the I/O module that needs to be replaced. A list of I/O modules can be found under the Options menu on the Device Specification page:
    1.JPG
     
  3. Find and record all input points on the I/O module to be replaced. This list is found in the I/O Configuration Table under the Options menu. For example, write the "Name" and "Bound To" address for every point referencing M2.
    2.JPG

     
  4. After you have noted all of the addresses for input points on the I/O module that will be replaced, you can edit the device type for the I/O module to reflect the new type (421A or 451A). Making this change WILL remove all DI mappings (421: X1-X4) and all thermistor mappings (451: B1-B4) affected by the change in module type.
    3.JPG

     
  5. Double-Click on each DI block from the 421 (X#) or on each AI thermistor input block from the 451 (B#) that you are updating to a 421A or 451A.
    4.JPG

     
  6. The following window will appear. Click the Bind button.
    5.JPG

     
  7. Update Menta
    1. FOR 421A POINTS:
      The controller’s DI points are now UI points. Select the Terminal Ref based on the old mapping:
      X1-U1, X2-U2, X3-U3, X4-U4
      6.JPG


      After selecting the new Terminal Ref, click the OK button and then the OK button again for the Edit Block window.
    2. FOR 451A POINTS:
      The controller’s thermistor inputs (B#) are now additional Universal Inputs. Select the Terminal Ref based on the old mapping:
      B1-U5, B2-U6, B3-U7, B4-U8
      7.JPG


      After selecting the new Terminal Ref, click the OK button and then the OK button again for the Edit Block window.
      **Repeat step 7 for all affected points on the I/O module you’ve updated.
  8. Repeat steps 2-7 for every I/O module that needs to be replaced by a 421A or a 451A.

PART II - Integration

  1. Within LonMaker locate the controllers that you want to change out for a 421A or 451A
    9.JPG

     
  2. Right click on them one by one, a click "Delete."
    10.JPG

     
  3. Open the Vista System Plug-In. Right click on the controller in which you want to change the .MTA application. Click "Configure."
    11.png

     
  4. Click "Browse," and locate the updated .MTA file you saved
    13.JPG

     
  5. Click "NO" when asked if you want to remove the devices
    14.JPG

     
  6. Click "Add and Match"
    15.JPG

     
  7. Click "Apply"
    17.JPG

     
  8. Re-Synchronize LonMaker
    19.JPG
    20.JPG
     21.JPG22.JPG23.JPG
  9. Your controllers should now be 421As or 451As
    24a.JPG24b.JPG25.JPG
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4856
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of