Replacements for the M52R and the EM52R damper actuators.
  • Replacements for the M52R and the EM52R damper actuators.
  • sesa125819
    sesa125819
‎2018-09-09 08:39 AM
What are the replacement for the M52R and the EM52R damper actuators?
Dampers
Actuators
The M52R and the EM52R damper actuators are obsolete.
When using either the M52R or the EM52R actuators to control dampers, the replacements are as follows;
The M52R actuator is a 24 volt drive open / drive close type, and is replaced by the MD10B-24.
The EM52R actuator is a 24 volt, 2 - 10 volt DC controlled  type, and is replaced by the MD10A-24.
For data sheets select below.
M52R / EM52R
MD10A-24
MD10B-24