Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Removing or deleting a SNVT programmed within a Xenta Device

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Removing or deleting a SNVT programmed within a Xenta Device
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • PeterLarsen
    PeterLarsen
  • Sacco
    Sacco
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1373 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Removing or deleting a SNVT programmed within a Xenta Device

Picard Product_Support
‎2018-09-06 02:14 PM

Issue

Removing or deleting a SNVT programmed within a Xenta Device that is no longer required in the application.

By removing SNVT you increase the chance of having difficulty of getting the LonMaker Template to synchronize correctly with the modified Menta file.

Understand the ramifications of deleting a SNVT and only do it when the benefits outweigh the complications.

Environment

  • TAC Vista
  • TAC Menta
  • NL220 or Lonmaker

Cause

Removing a SNVT will upset the SNVT binding order, by causing the index numbers in the XIF file to be corrupted. In this case it is not advised to delete SNVTS

Changing a SNVT name or type will also cause indexing problems.

The Vista object name can be changed to reflect that the SNVT is spare and not used

If you have no SNVTs bound in LonMaker, the cost of deleting a SNVT is potentially having difficulty getting your LonMaker device template to synch up with the Menta file. If you have a few bindings, the downside of deleting a SNVT also includes redoing all of the bindings -- with one or two that's not a big deal. If you have 200 bindings, it can be a huge deal. Leaving a SNVT in the Menta file that isn't being used anymore just consumes one network variable input ... which can usually be dealt with easier than deleting it. So it's just weighing the pros and cons, but don't just go through without knowing what will happen.

Resolution

If the SNVT is no longer required in the Menta Application then carry out these steps.

  1. Disconnect the SNVT from the logic in the Menta application
  2. Allocate an area in you Menta application for unused SNVTs
  3. Move your unused SNVT into this area
  4. Label this area with the Text "UNUSED SNVTS DO NOT DELETE"
  5. Remove the public check box from the point if you do not want it visible in Vista
  6. Download the Menta application to the Xenta controller.

Note: If the Xenta Application is standalone (Classic) and not in a LNS database SNVTs can be deleted without a problem

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4410
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore