Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Remove Unknown Embedded Demo License

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Remove Unknown Embedded Demo License
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • PeterEdvik
    PeterEdvik
  • RobertAndriolo
    RobertAndriolo
  • MikaelKrantz
    MikaelKrantz
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
3476 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Remove Unknown Embedded Demo License

Guinan MikaelKrantz Guinan
‎2022-11-24 01:49 AM

Last Updated: Administrator CraigEl Administrator ‎2024-09-06 12:39 AM

Issue

How to remove an unknown Embedded Demo License

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Automation Server Premium (AS-P)
  • Device Administrator v4.0.5 (EBO 2022) and below

Cause

The Embedded Demo Licenses are handled from the Device Administrator software.
However, if the installed Embedded Demo License in the SpaceLogic servers does not comply with the file in the Device Administrator, the installed Demo License could not be removed.

Resolution

Instructions shown in the video below are for EBO 2022 (v4.0.5) and below. In the later releases EBO 2023 (v5.x) and above, a feature now allows the Demo licenses to be returned from selected servers.  See WebHelp topic Returning All Demo Licenses from the Selected SpaceLogic Automation Servers 

For any License activations/returns to occur, there must be a trusted state (Certificate State) between the server and Device Administrator. Ensure that this is in place before attempting either resolution. For more info, see Certificates Managed using Device Administrator

 

If this function does not work, you can attempt the manual file name manipulation described below. 

 

To check the name of the installed Embedded Demo License, log in to the SpaceLogic servers from Workstation.

Navigate to System, LicenseManager, LicensingMetadata, ClientMetadata, Product 0.

In ProductID, you will see the filename of the actual file.

 

Rename a Demo license file and import it into Device Manager to uncheck the selected Demo License file.

 

At the end of this session, you will be able to:

  • Remove Unknown Demo License in SpaceLogic servers

 

[video]

 

 

 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • HernanUruena24
  • MikaelKrantz22
  • RobertAndriolo24
Was this article helpful? Yes No
75% helpful (3/4)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore