Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Remote Alarm Manager settings are lost after upgrade.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Remote Alarm Manager settings are lost after upgrade.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
841 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Remote Alarm Manager settings are lost after upgrade.

Picard Product_Support
‎2018-09-06 02:47 PM

Issue

After upgrading Remote Alarm Manager 1.2 to 2.0 none of the settings site specific configuration is carried over and Remote Alarm Manager can't detect the license.

Environment

Sigma 4

Remote Alarm Manager 2.0

Cause

The site has upgraded Remote Alarm Manager through several iterations over time, versions of Remote Alarm Manager prior to version 1.001 stored site configuration data with the source system data. For example in the C:\Sigma\Data\Remote Alarm Manager\ folder, current versions typically store the data by default in:-

  • For Windows XP - C:\Documents and Settings\All Users\Application Data\Schneider Electric\Remote Alarm Manager.
  • For later operating systems - C:\ProgramData\Schneider Electric\Remote Alarm Manager.

Resolution

There are two possible ways to resolve the issue:-

  1. After installation of the software run the Computer Configuration utility (this runs by default) and deselect (uncheck) the Windows
    Common Application Data checkbox on the "Data Location" tab and enter the path to the current Remote Alarm Manager data location.
  2. After Installing the software and running the Computer Configuration utility copy the setup.mdb and log.mdb files from the current location to the default location used by the software:-
    • For Windows XP - C:\Documents and Settings\All Users\Application Data\Schneider Electric\Remote Alarm Manager.
    • For later operating systems - C:\ProgramData\Schneider Electric\Remote Alarm Manager.
Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (1)
  • Find more articles tagged with:
  • 11807
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now