Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Remote Alarm Manager (RAM) – Engine Fails to Start or Shuts Down Unexpectedly

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Remote Alarm Manager (RAM) – Engine Fails to Start or Shuts Down Unexpectedly
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support
  • sesa125819
    sesa125819

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1489 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Remote Alarm Manager (RAM) – Engine Fails to Start or Shuts Down Unexpectedly

Picard Product_Support
‎2018-09-07 11:22 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-08 07:45 PM

Issue

The Remote Alarm Manager (RAM) engine either:

  • Fails to start, or
  • Shuts down unexpectedly during normal operation.

Product Line

Satchwell BAS & Sigma

Environment

  • Satchwell Sigma
  • Satchwell BAS 2800+
  • TAC Vista
  • Satchwell Micronet
  • Remote Alarm Manager

Cause

The issue is typically caused by the Log.mdb file growing excessively large. This file logs:

  • System alarms
  • User actions
  • RAM system actions

Since there is no size limit on this file, it can consume excessive memory, leading to RAM instability or shutdown.

    1. Resolution

      Manage the Log.mdb File

      To prevent the file from growing uncontrollably:

      • Stop RAM services.
      • Navigate to the Log.mdb file location (commonly found at:
        Sigma\\Data\\Remote Alarm Manager).
      • Delete or rename the Log.mdb file.
      • Restart RAM services – a new Log.mdb file will be automatically created.

      🔁 Best Practice: Perform this cleanup regularly if the system is stable.

    2. Adjust Logging Settings

      Reduce the frequency and verbosity of logging to minimize file growth:

      • Navigate to the Debugging screen for the relevant interface (e.g., GSM Modem).

      • Set the logging level to one of the following:
        • Nothing – No logging (recommended if RAM is stable)
        • Errors – Logs only error messages (recommended)
        • Normal – Logs low-level operational info
        • Detailed – Logs more in-depth data
        • Verbose – Logs all available information (not recommended for production)

          ✅ Recommendation: Use “Nothing” or “Errors” for stable systems to reduce log file size and improve performance.

Labels (3)
Labels:
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 5090
  • CraigEllis25
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore