Remote Alarm Manager - Alarm message script required to show date and time.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Remote Alarm Manager - Alarm message script required to show date and time.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • sesa125819
    sesa125819

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1151 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Remote Alarm Manager - Alarm message script required to show date and time.

Picard Product_Support
‎2018-09-07 11:37 PM

Issue

The date and time must be included in the text message.

Environment

Sigma

Micronet

Vista

BAS2800+

RAM

Remote Alarm Manager

Cause

The basic text messages do not include the alarm date and time, this is a site requirement..

Resolution

To change the message format, configure as follows:

1 - Using the RAM Console, select "Configuration" and the required "Action".

2 - Edit the Action, and select "Messages".

3 - Choose the "Advanced" option, and then "Edit Script".

4 - Choose "File" and then "Open File", browse to the location of the script file you want to open. An example script file can be uploaded from here.

5 - The screen capture below shows part of the script editor with the script file opened.

This script will provide an alarm message which takes the following form.

Message No (This cannot be de-configured), Alarm Priority, Alarm Date / Time, Mnemonic, and Value (i.e. Plant On / Plant Off etc.).

The alarm cleared message is slightly different.

Message No (This cannot be de-configured), Alarm Date / Time, Mnemonic, and Value (i.e. Plant On / Plant Off etc.).

Labels (3)
Labels:
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC Vista
Attachments
RAM Script.zip
Tags (1)
  • Find more articles tagged with:
  • 5109
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of