Release the freed-up disk space from Extended Log Storage (PostgreSQL/TimescaleDB) back to Windows.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Release the freed-up disk space from Extended Log Storage (PostgreSQL/TimescaleDB) back to Windows.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1728 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Release the freed-up disk space from Extended Log Storage (PostgreSQL/TimescaleDB) back to Windows.

Lieutenant | EcoXpert Master SangKim Lieutenant | EcoXpert Master
‎2022-08-23 08:56 AM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:33 AM

Issue

After deleting unnecessary TrendLog objects from EBO and their logged data from the Extended Log Storage (PostgreSQL/TimescaleDB) by selecting the “Clear log” from the System folder (i.e.: Server1/System/Extended Log Storage/TimescaleDB/Trend/Tree View/…”), the Windows still shows the same free disk space size as it was before the deletion.

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Enterprise Server
  • Building Operation Automation Server
  • External Log Storage
  • PostgreSQL (pgAdmin 4)
  • TimescaleDB 

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Cause

PostgreSQL databases require periodic maintenance known as vacuuming for Windows to recover or reuse the freed-up disk space occupied by PostgreSQL/TimescaleDB.

Resolution

There are two variants of VACUUM: standard VACUUM and VACUUM FULL.  VACUUM FULL can reclaim more disk space but runs much more slowly.  VACUUM FULL requires an exclusive lock on the table it is working on, and therefore cannot be done in parallel with other use of the table. Refer to the documentation mentioned at  https://www.postgresql.org/docs/9.5/routine-vacuuming.html  before performing the VACUUM command.

 

Below is an example of the procedure to get the freed-up disk space occupied by PostgreSQL/TimescaleDB back to Windows.

 

1. Back up the current PostgreSQL/TimescaleDB database and save to a safe location.

  1. Backup the “ebo_db” from the PostgreSQL/TimescaleDB server using the pgAdmin 4 (refer to https://www.pgadmin.org/docs/pgadmin4/development/backup_dialog.html , or refer to page 8 “Backup” section of the “EBO External Log Storage Installer.pdf” document for detail).

 

2. Stop the External Log Storage from EBO.

  1. Open the Properties of the TimescaleDB object (/Server/System/External Log Storage/).\
  2. Remember (take a note) the current value settings of the “Host Address” & the “Database Name” attributes.
  3. Change them to the wrong value (or clear them) so that EBO fails to connect to the PostgreSQL/TimescaleDB server.
  4. Repeat the above operation for all the other servers (AS’s) that are enabled/connected to the PostgreSQL/TimescaleDB server.

 

3.Delete the old logs from the PostgreSQL/TimescaleDB database (the “ebo_db”).

  1. Run the pgAdmin 4, select the “ebo_db”, open the “Query Tool”, and execute the below scripts:

  Delete from trend_data where DATE_PART('day', now() - timestamp) > 365

  Delete from event_data where DATE_PART('day', now() - timestamp) > 365

 

4. Vacuum the Database with Full option.

  1. From the same Query Tool on the “ebo_db”, run the below command: Vacuum Full
  2. Wait until it completes (this may take a while depending on the number of old logs that have been deleted from the tables).

 

5. Start the External Log Storage from EBO.

  1. Open the Properties of the TimescaleDB object (/Server/System/External Log Storage/).
  2. Set the value of the “Host Address” & the “Database Name” back to the correct value, so that the EBO server successfully connects to the PostgreSQL/TimescaleDB server.
  3. Verify the EBO server is connected to the PostgreSQL/TimescaleDB server, and it works normally.   
  4. Repeat the above operations for all the other EBO servers (AS’s) that were disabled/disconnected from the PostgreSQL/TimescaleDB server.

 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • external
  • SangKim22
  • storage
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore