RM3601 / XRM3201 Wiring connection details.
RM3601
3601
XRM3201
3201
Actuators
Wiring
connection details
Actuator wiring details.
The RM3601 actuator is a 230 volt actuator, its connection details are as follows;
Terminal 1 - Connection for open signal (230V live)
Terminal 2 - Connection for close signal. (230V live)
Terminal 3 - Connection for Neutral.
Terminal 1T - Transfer connection, passes 230V to other devices when actuator is open.
Terminal 2T - Transfer connection, passes 230V to other devices when actuator is closed.
The XRM3201 actuator is a 24 volt actuator, its connection details are as follows;
Terminal 1 - Connection for open signal (24 volts)
Terminal 2 - Connection for close signal. (24 volts)
Terminal 3 - Connection for zero volt.
Terminal 1T - Transfer connection, passes 24V to other devices when actuator is open.
Terminal 2T - Transfer connection, passes 24V to other devices when actuator is closed.