RAW alarms seen in alarm or error log
  • RAW alarms seen in alarm or error log
  • Dave_Shore
    Dave_Shore
  • PaulFr
    PaulFr
  • JohnBoehmer
    JohnBoehmer
‎2018-09-06 10:45 AM
What can cause RAW alarms seen in alarm log?
Continuum error alarm log
List View
The two most common reasons for seeing Raw Alarm Errors are...
  • Alarms have been updated or deleted offline
  • Continuum DB server is being overloaded.
    • When this occurs, the alarm event coming off the wire gets dropped in the Raw alarm table to get its name and all other information rendered out into a readable format.
    • If the server is too backlogged the alarm could fall off the raw alarm table before the rendering is complete which in turn would generate the Raw Alarm error.
  • If the alarm has been updated or deleted offline, reloading the controllers should remove these RAW alarm errors.  This will ensure the database is fully synchronized with the controllers.
  • If there are indications that SQL is overburdened steps should be taken to address this issue.