RAM Remote Alarm Manager Message: Alarm on GSM Modem – Unable to Reset GSM Modem

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • RAM Remote Alarm Manager Message: Alarm on GSM Modem – Unable to Reset GSM Modem
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • sesa139513
    sesa139513
  • DavidChild
    DavidChild
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1271 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

RAM Remote Alarm Manager Message: Alarm on GSM Modem – Unable to Reset GSM Modem

Picard Product_Support
‎2018-09-06 10:32 AM

Last Updated: Administrator CraigEl Administrator ‎2025-10-20 06:39 PM

Issue

The Remote Alarm Manager (RAM) displays the following error message:

"Alarm on GSM modem – Unable to reset GSM modem – modem did not accept reset command"

This issue indicates that the GSM modem has stopped responding and cannot be reset via the standard command.

Product Line

Satchwell BAS & Sigma

Environment

Remote Alarm Manager (RAM)

Cause

This issue typically occurs when the GSM modem interface becomes unresponsive. It may be due to:

  • Communication failure between RAM and the GSM modem
  • Incompatibility or malfunction of the serial PCI / PC Express card
  • Incorrect or incompatible driver installation
  • Insufficient retry attempts or timeout settings in the modem configuration

Resolution

 

  • Verify Modem Configuration:

    • Check the modem type and ensure it is supported.
    • Navigate to the Advanced tab in the modem settings.
    • Increase the number of retries and response timeout values to allow more time for the modem to respond.
  • Use a USB to Serial RS232 Adapter (Workaround):

    • If the issue persists, consider replacing the PCI / PC Express card with a USB to Serial RS232 adapter.
    • Ensure the correct driver is installed for the adapter. For example:
      • StarTech FTDI USB to Serial RS232 Adapter (Part No. ICUSB2321FIS) requires the FTDI driver, not the Prolific driver.
    • After installation:
      • Open Device Manager in Windows.
      • Locate the newly created serial COM port assigned to the USB device.
      • Reassign the GSM modem in RAM to use this new COM port.

 

Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (2)
  • Find more articles tagged with:
  • 12862
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore