Program IDs do not match. There is an incorrect or out-of-date program version. (Subsystem: NS, #38)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Program IDs do not match. There is an incorrect or out-of-date program version. (Subsystem: NS, #38)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • DavidFisher
    DavidFisher
  • sesa119747
    sesa119747
  • Sacco
    Sacco
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
5491 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Program IDs do not match. There is an incorrect or out-of-date program version. (Subsystem: NS, #38)

Picard Product_Support
‎2018-09-07 03:11 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-11-04 09:19 AM

Issue

NS38.png

Program IDs do not match. There is an incorrect or out-of-date program version. (Subsystem: NS, #38)

Product Line

TAC Vista

Environment

  • LonMaker 3.X
  • NS Error codes are not specific to any one LON environment, the display of the error may vary, but the steps to resolve should be the same.

Cause

A Program ID is a unique identifier assigned to each XIF (or device template) in an LNS database. Controllers with different XIFs cannot share the same Program ID. When a device is created in an LNS database, its Program ID is extracted from the XIF and stored in the database. When a controller is downloaded, the Program ID is transferred and stored in the controller. If the Program ID that resides in the controller differs from the one stored in the LNS management tool, the commission command will fail due to the Program ID mismatch.

Resolution

The appropriate resolution to the NS, #38 error depends on which controller is failing to commission. Select from the categories below which best describes the offending controller. 

Xenta Programmables (follow steps below)
Xenta 28X, 30X, 401(:B)

  1. Download the controller through the Vista System Plug-in before attempting to commission.
  2. If the error remains after a download, then the download did not go through, despite all indications that it did. Connect to the RS-232 serial port of the controller and attempt to download the Menta file directly. This will often bring to light parsing errors that are not detected by the System Plug-in.
  3. Find and correct the errors to allow the file to download properly. See Menta Parser Errors for more information on parser errors. The controller should then commission successfully.

    --- If the error persists, continue ---
     
  4. Open the Menta file of the controller that will not commission. Under Options > Device Specification, uncheck the box for "XIF-Header generated according to LonMaker standard." (You may have to temporarily assign a System Version to activate this checkbox.)
  5. LonMark standard headings only use 255 combinations of IDs. It may be that two controllers just happened to be assigned the same Program ID. After unchecking this box, go to Options > Simulate, Commands > Generate to regenerate a new Program ID without using the LonMark standard header which opens up many more Program ID combinations and lessens the already low probability of two being the same.
  6. Download the new Menta file with the new XIF and new Program ID into the controller. It should now commission successfully.

 

Xenta 5/7/9XX
Xenta 511, 527, 701, 711, 721, 731, 913

  1. The XIF in the LNS database must be updated.
  2. See How to update a modified Xenta 5/7/9xx XIF file in LonMaker for detailed instructions.

 

ASCs/LON Devices (choose an option below)
Xenta 100 series, third-party devices

  1. Replace the device using the correct XIF obtained from the manufacturers website.
  2. Replace the device using the correct XIF obtained from https://www.lonmark.org/.
  3. Replace the device with a generic device. Commission with the option of getting the XIF from the device.

 

Xenta 400 Series I/O Module (choose an option below)
Xenta 42X(A), 45X(A), 47X, 49X

  1. Be sure the correct module is defined in Menta if adding I/O modules automatically.
  2. If adding I/O modules manually, be sure to use the correct stencil on the LonMaker drawing. You will get this error if you try to commission a 451A module with a 451 stencil.
Labels (1)
Labels:
  • TAC Vista
Tags (18)
  • Find more articles tagged with:
  • 280
  • 281
  • 282
  • 283
  • 300
  • 301
  • 302
  • 3886
  • 401b
  • 411
  • 421
  • 421a
  • 422
  • 422a
  • 452
  • 452a
  • 471
  • 491
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of