Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Procedure to replace Satchwell MicroNet controller with Satchwell MicroNet 50 series controllers

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Procedure to replace Satchwell MicroNet controller with Satchwell MicroNet 50 series controllers
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Gary
    Gary
  • RyanSuar
    RyanSuar

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2130 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Procedure to replace Satchwell MicroNet controller with Satchwell MicroNet 50 series controllers

Picard Product_Support
‎2018-09-10 01:20 AM

Last Updated: Administrator DavidFisher Administrator ‎2019-09-30 04:29 AM

Issue

Procedure to replace Satchwell MicroNet MN300, MN440, MN500 or MN620 controller with Satchwell MicroNet 50 series controllers MN350, MN450, MN550 or MN650

Environment

  • Satchwell MicroNet series controllers:
    • MN300, MN440, MN500, MN620
    • MN350, MN450, MN550, MN620
  • Satchwell VisiSat version 2.1 and above.

Cause

Satchwell MicroNet series MN300, MN440, MN500 and MN620 are no longer available for sale and they are replaced by the MN350, MN450, MN550 and MN650 controllers respectively. See Product Announcement for details.
MN300, MN440, MN500 and MN620 controllers installed on existing installations that are required to be replaced would have to be replaced with the new range of controllers.

Resolution

To replace Satchwell MicroNet MN300, MN440, MN500 or MN620 controller with Satchwell MicroNet 50 series controllers MN350, MN450, MN550 or MN650 follow the procedure below.

  1. Pre-VisiSat 2.1 projects (VisiSat 1.2 and VisiSat 2.0) should be upgraded to VisiSat 2.1 using the Project Upgrade Utility.
    Download VisiSat 2.1 Engineering Guide here.
    Refer to pages 47 - 50 for using the Project Upgrade Utility
  2. Open the VisiSat project
  3. Right-click on the existing controller and select "Upgrade Controller."
  4. There is a prompt to save the controller configuration (.CLC file). Select 'Yes'.
  5. The controller object in VisiSat will now be converted to a MN50 Series controller.
  6. Replace the controller hardware. Make sure the jumpers are set correctly and that communications card, if existing should  be taken out and installed into the new controller.
  7. Right-click on the controller object in VisiSat and select 'Configuration Library'. Select 'Download Configuration' (2nd button from the left in the Configuration Library). This will download the configuration to the new controller.
    Refer to pages 135 - 140 in the VisiSat 2.1 Engineering Guide for using the Configuration Library.

NOTE: In the Configuration Library, the first button from the right is the "Upgrade Controller" option. This performs the same function as the "Upgrade Controller" mentioned in step 3 above.

Labels (1)
Labels:
  • Satchwell MicroNet
Tags (1)
  • Find more articles tagged with:
  • 5964
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of