Issue
In a MicroNet MN 550 controller, the output of Instance 31 of the Priority Value Select object consistently returns a value of 0, while all other instances function correctly.
Product Line
Satchwell MicroNetEnvironment
MicroNet MN 550 controller
Cause
This issue occurs due to a firmware limitation in earlier versions of the MicroNet 50 controller. Specifically, Instance 31 does not behave as expected unless the controller is updated.
Resolution
Upgrade the MicroNet 50 controller to Firmware Version 5, released in August 2008. This version resolves the issue with Instance 31.
- Refer to TPA-LOND-08-0014.00 for detailed information about Firmware Version 5.