Issue
When a special event time period overlaps with a public holiday where the calendar day is set to OFF, the system still runs according to the special event. Users need clarity on the priority between:
- Special events
- Holiday overrides
- Weekly time schedules
Product Line
TAC IA SeriesEnvironment
I/A Series R2 schedule and calendar objects
Cause
Resolution
According to the Niagara Standard Programming Reference, schedule evaluation follows this priority (highest to lowest):
- overrideIn input (if linked)
- Special Events – replaces holiday and weekly events
- holidayOverride input (if linked) – replaces weekly events
- Weekly schedule – normal time-of-day events
Important: When programming special events, include any scheduled and holiday actions applicable for that day within the special event configuration.