TAC IA SeriesEnvironment
Niagara R2
routeAcks property set to True, which routes acknowledgment events to email recipients.Resolution
To prevent emails from being sent when alarms are acknowledged:
Open MailRecipient Configuration
- Navigate to the MailRecipient object in the Niagara R2 station.
Modify routeAcks Property
- Go to the Config tab.
- Set the
routeAcksproperty to False.
Apply Changes
- Click Apply to save the configuration.
After this change, acknowledgment events will no longer trigger email notifications.