Point in MP-x contains unresolved BACnet reference
  • Point in MP-x contains unresolved BACnet reference
  • JohnBoehmer
    JohnBoehmer
  • RobertAndriolo
    RobertAndriolo
  • AbeMeran
    AbeMeran
Captain AbeMeran Captain
‎2019-05-21 07:39 AM
Last Updated: Picard RobertAndriolo Picard ‎2019-06-17 07:48 PM
Point under the Application folder of MP-x device shows error "Contains unresolved BACnet reference"
  • Building Operation Multi-purpose Controller
  • Building Operation Multi-purpose VAV
  • Building Operation IP-IO
Incomplete entry in point's BACnet priority array.
The screenshot below shows the XML file obtained from exporting the point, as it can be seen, 'Priority16' is missing the 'Type' section.
Perform the following steps to correct the problem:
  1. Export the point out to a file.
  2. Delete the point.
  3. Import the file created at step 1, once the point has been re-created via import the unresolved error is gone.
NOTE:
There is no need to make any modifications to the XML file, it can be imported as is, the system will automatically correct the incomplete entry for priority16.
  • AbeMeran19
84% helpful (5/6)