Pictures, animations and bitmaps in a Sigma graphic fail to appear when upgraded from Sigma 4.04 to Sigma 4.05 or above.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Pictures, animations and bitmaps in a Sigma graphic fail to appear when upgraded from Sigma 4.04 to Sigma 4.05 or above.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • sesa139513
    sesa139513
  • DavidFisher
    DavidFisher
  • DavidChild
    DavidChild
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1425 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Pictures, animations and bitmaps in a Sigma graphic fail to appear when upgraded from Sigma 4.04 to Sigma 4.05 or above.

Picard Product_Support
‎2018-09-10 11:24 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-08 10:17 PM

Issue

After upgrading from Sigma 4.04 to Sigma 4.05 or above, pictures, animations, and bitmaps in Sigma graphics may fail to appear.

Product Line

Satchwell BAS & Sigma

Environment

  • Sigma 4.04
  • Sigma 4.05 and above

Cause

During the upgrade process, graphics originally in .sgi format are converted to .swc format. If the original graphic had broken or missing links to image files, these links will not be carried over. As a result:

  • The viewer window may appear empty or show placeholder content.
  • The image files are not created in the new path:
    C:\Sigma\Data\Graphics\
  • This typically occurs if the image was not installed correctly or saved after the link was lost.

Resolution

Option 1: Pre-upgrade Fix (Recommended)

  1. Open the graphic in .sgi format.
  2. Highlight an image and right-click → Properties.
  3. Verify the image link:
    • If the link is active, the image will be highlighted with a grey background.
    • If not, re-establish the link by locating the correct image file.
  4. Save the graphic.
  5. Proceed with the upgrade to .swc format.

Option 2: Post-upgrade Fix

  1. Manually copy the image folders from:
    C:\Sigma\Data\Sgi\
    to:
    C:\Sigma\Data\Graphics\
  2. Open the graphic in .swc format.
  3. Re-establish the image links by locating the correct files.
  4. Save the graphic.
Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (2)
  • Find more articles tagged with:
  • 12242
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore