Permanently unlock Door with Triple Badging at the Door

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Permanently unlock Door with Triple Badging at the Door
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • AdamSteele
    AdamSteele

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1241 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Permanently unlock Door with Triple Badging at the Door

Guinan AdamSteele Guinan
‎2019-11-11 01:46 AM

Issue

Require method on how to latch unlock a Door by Triple Badging.

Product Line

EcoStruxure Security Expert

Environment

Security Expert

Cause

Require Door to be controlled normally with card access but also to allow a valid User to latch unlock the Door with three consecutive valid badges.

Resolution

Required Objects

  • virtual Output - Flag to trigger latching (v_TripleBadgeLock)
  • Programmable Function - Latches Door when virtual output ON (Door_UnlockLatch)
  • Programmable Function - Unlatches when virtual output OFF (Door_UnlockLatch_Restore)
  • Door - Door to control (MainEntrance)

Configuration

  1. Create virtual Output v_TripleBadgeLock. Set Module Type to Output (PX) and Module Address and Module Output channel to ones that do not exist.
    Virtual OutputVirtual Output
  2. On the Reader Expander > Reader 1 tab
    - Set Reader 1 Arming Mode to Toggle Function Output on 3 Reads
  3. Set Reader 1 Function Output to v_TripleBadgeLock
    Reader Expander - ConfigurationReader Expander - Configuration
  4. Go to Automation > Programmable Functions and create Door_UnlockLatch 
    - Set Type to Door Control
    - Set Mode to Normal
    Programmable Function - GeneralProgrammable Function - General
  5. Under Door Control tab
    - Set Door Function Mode to 2 - Follow Pulse On Output
    - Set Door Control Mode to 1 - Latch Door Unlock
    -
    Set Output To Check to v_TripleBadgeLock
    -
    Set Door To Control to MainEntrance
    - Save changes
    - Right-click Door_UnlockLatch function and select Start
    Programmable Function - UnlockLatch - Door ControlProgrammable Function - UnlockLatch - Door Control
  6. Go to Automation > Programmable Functions and create Door_UnlockLatch_Restore
    - Set Type to Door Control
    - Set Mode to Normal
  7. Under Door Control tab
    - Set Door Function Mode to 5 - Inverted Follow Pulse Off Output
    - Set Door Control Mode to 0 - Emulate Unlock Menu
    - Set Output To Check to v_TripleBadgeLock
    -
    Set Door To Control to MainEntrance
    -
    Save changes
  8. Right-click Door_UnlockLatch_Restore function and select Start
    Programmable Function - Unlatch - Door ControlProgrammable Function - Unlatch - Door Control
Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (1)
  • Find more articles tagged with:
  • AdamSteele23
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of