Performing database maintenance with Vista 4.5.0

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Performing database maintenance with Vista 4.5.0
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1980 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Performing database maintenance with Vista 4.5.0

Picard Product_Support
‎2018-09-07 01:48 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:54 AM

Issue

Performing database maintenance with Vista 4.5.0

Product Line

TAC Vista

Environment

  • Vista 4.5.0
  • SQL Server

Cause

It is necessary to perform backups for two reasons, first to be able to recover the system in the event of a fatal error and second to be able to manage the size of the database.

Resolution

Vista has a means of backing up databases on a Vista Server.  It is necessary to perform backups for two reasons, first to be able to recover the system in the event of a fatal error and second to be able to manage the size of the database.  The Vista database probably won’t grow very much after the initial engineering activity but the event and trend log database grows as events are received in Vista.  In many installations maintaining an archive of event data is required so that is another reason for backing up the database.  This paper presents a way to accomplish the backing up of the Event and Trend database and creating an archive file.

Before the backup process can be implemented it is first necessary to have a good estimate of the Event and Trend Log traffic anticipated for the installation.  In the Vista 4.3.0 Technical Product Information (TPI), Ref No: C88-1-D43, there is section entitled Strategies for Calculating and Controlling Database Size.  On page 5 the method for determining database size is explained and used in the following example:

Right clicking on the $Backup_LDB object in the Server View brings up this dialog.

backupldb.png

 

Note that this example has an Event and Trend database that has reached 1121 (MB) in size.  The default Size Alarm Limit is shown to be 1640 and if the database grows past that size, Vista may not operate reliably.

The TPI states on page 4 that events contain on average 2Kb of data.  Combining that value with the expected traffic provides a reasonable estimate of the database expansion rate.  If the installation traffic estimate is 4000 Events and Trend samples per day, the database expands at the rate of 8Mb per day.  If the installation traffic estimate is 10,000, the database expands at the rate of 20Mb per day.

A conservative approach would limit the size of the active database to half of the alarm limit.  That means the backup process must be done so that the size does not get to 820Mb.  At 10000 Events and Trend samples per day that value would be reached every 41 days.  Vista is designed to allow Event driven backup operations and the closest choice it offers to the 41 days is once a month so that is what will be chosen.

The configuration of backup is done in Vista Workstation by opening the Properties of the Workstation object in the tree.  The first step is to select a location for the backup files to be saved.  In the example shown below it is the folder outlined in red.

backupfile.png

 

The “Max number of files” limits the number of backups that are retained by Vista on the hard drive.  The number chosen here was two (2).  The procedure that is described further down will actually move backup files to new directories which could be a network drive or a CD/DVD rom.  (The latter option requires operator action so it might not be the most desirable especially since backups are usually done at off times when an operator might not be available) 

Next the event that is to trigger the backup must be defined.  The configuration of when the backup is done is set on the Log Backup tab of the Vista Server Properties dialog.  In the example shown below the backup is scheduled to occur on the first of every month at 12:40AM. The selection of Event object is made from the options made available by the browse button.browse.png

 

eventldb.png

 

The browse selection brings up the Select dialog from which the selection of Event type and properties is done.  In the following example the selection is Monthly.

select.png

 

Right clicking on the $Event_LDB object opens the properties dialog box to configure the Event_Month object. 

The final configuration option is what to do with older records.  Vista will remove Events from the database if you so desire.  The removal does not shrink the database but does make space available for new events to be written without expanding the size of the database.  This is the key to keeping the database from exceeding the Alarm Limit.

The Event Log tab provides a way to delete old records from the database.  In the example shown below records older than 30 Days will be deleted after the backup that was done be the Event_Month object has been completed.  This means that each month the backup should have the most recent 30 days of Events and Trend samples.

evlog.png

 

The final step that can be taken is to also copy the backup file to a server that is backed up or to a CD/DVD Rom. This operation creates an archive in which Event and Trend data is stored.  Windows task scheduler can be used to run a cmd at some time after the backup operation was scheduled.  For the above example schedule it to run a 1:00am on 1st of each month.  If backing up to a network drive create a folder such as shown below. 

J:\Engineering\Vista Event Log BU. 

In order for the task scheduler to run it is necessary to setup a user account on the pc that is not related to any actual user.  I added a user to the User group named,

vista xcopy dbmgr. 

This will be the user account used by the task scheduler.  The Vista backup folder must have modify/write permissions for this user and the folder into which the backup is going to be copied must have Full control.

computermanagement.png

 

The command line for this example is shown below:

C:\WINDOWS\SYSTEM32\xcopy.exe "C:\Program Files\TAC\TAC Vista 4.5.0\Db2\$bkp" "J:\Vista Event Log BU" /M

The Windows task scheduler is configured in the Control Panel, Scheduled Tasks as shown below:

xcopy.png

 

In the Run as: box enter the name of the new User created described above:

vista (xcopy dbmgr)

Schedule the task to run on the first of each month at 1:00AM.

xcopyschedule.png

 

The backup files can be restored to a Vista Server that is not performing actual site monitoring.  This method is only way the “archived” event and trend data can be viewed as of Vista revision 4.5.0.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 2153
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore