Overriding Values in a Xenta 102-AX without the Plug-In

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Overriding Values in a Xenta 102-AX without the Plug-In
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1513 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Overriding Values in a Xenta 102-AX without the Plug-In

Picard Product_Support
‎2018-09-06 02:01 PM

Issue

Certain values in the Xenta 102-AX can be put into override mode through the Plug-In:

  • Airflow
  • Auxiliary Temperatures 1 and 2
  • Universal Inputs 1, 2, 3, and 4
  • CO2
  • Space Temp
  • Damper Position
  • Universal Outputs 1, 2, and 3

If the plug-in is not available, they can be overridden through the SNVT input nviRequest (type SNVT_obj_request).

Product Line

EcoStruxure Building Operation, TAC Vista

Environment

Xenta 102-AX

Cause

The plug-in might not be available for a multitude of reasons. For example, if the Xenta 102-AX is being integrated into a third party LON system, or no LNS management tool is being used. The values below can be used to implement an override through the SNVTs.

Resolution

Signals required to perform external control of inputs and outputs on the Xenta 102-AX:

  1. Set the override behavior value signal to 1 (OV_SPECIFIED)
  2. Set the desired value in the override value signal
  3. Send a SNVT to the signal Node_Object.nviRequest. It is a structured SNVT input with the following members:
    1. OBJECT_ID - refer to the list below for the appropriate object ID for each override
    2. OBJECT_REQUEST - set to value to 6 (RQ_OVERRIDE) to initiate the override, set to value 0 (RQ_NORMAL) to release the override.

The tables below specify all necessary signals for each override. They are displayed in the following format:

ID Title
Overridden Value
Desired Override Value
Override Behavior

 

1 Airflow Reading (CFM, l/s)
Airflow_Sense.nvoAirFlow.PV
Airflow_Sense.nvoAirFlow.SCPTovrValue.PV
Airflow_Sense.SCPTovrBehave.PV

 

2 Universal Input 1 (%)
UnivIn1_Sense.nvoUnvInput1.PV
UnivIn1_Sense.nvoUnvInput1.SCPTovrValue.PV
UnivIn1_Sense.SCPTovrBehave.PV

 

2 Duct Inlet Temperature UI1 (°F, °C)
UnivIn1_Sense.nvoAuxTemp1.PV
UnivIn1_Sense.UCPTovrValueTemp.PV
UnivIn1_Sense.SCPTovrBehave.PV

 

3 Universal Input 2 (%)
UnivIn2_Sense.nvoUnvInput2.PV
UnivIn2_Sense.nvoUnvInput2.SCPTovrValue.PV
UnivIn2_Sense.SCPTovrBehave.PV

 

4 Universal Input 3 (%)
UnivIn3_Sense.nvoUnvInput3.PV
UnivIn3_Sense.nvoUnvInput3.SCPTovrValue.PV
UnivIn3_Sense.SCPTovrBehave.PV

 

4 CO2 Reading UI3 (ppm)
UnivIn3_Sense.nvoCO2sensor.PV
UnivIn3_Sense.UCPTovrValueCO2.PV
UnivIn3_Sense.SCPTovrBehave.PV

 

4 Outside Air Temperature UI3 (°F, °C)
UnivIn3_Sense.nvoAuxTemp2.PV
UnivIn3_Sense.UCPTovrValueTemp.PV
UnivIn3_Sense.SCPTovrBehave.PV

 

5 Universal Input 4 (%)
UnivIn4_Sense.nvoUnvInput4.PV
UnivIn4_Sense.nvoUnvInput4.SCPTovrValue.PV
UnivIn4_Sense.SCPTovrBehave.PV

 

5 Setpoint Offset UI4 (°F, °C)
UnivIn4_Sense.nvoSetPtOffset.PV
UnivIn4_Sense.UCPTovrValueTemp.PV
UnivIn4_Sense.SCPTovrBehave.PV

 

6 Space Temperature (°F, °C)
VAV_Controller.nvoSpaceTemp.PV
VAV_Controller.nviSpaceTemp.SCPTovrValue.PV
VAV_Controller.SCPTovrBehave.PV

 

7 Damper Actuator (%)
Damper_Actuator.nviRelStPt.PV
Damper_Actuator.nvoActualValue.SCPTovrValue.PV
Damper_Actuator.SCPTovrBehave.PV

 

8 Universal Output 1 (%)
UnivOut1_Object.nviUnvOutput1.PV
UnivOut1_Object.nviUnvOutput1.SCPTovrValue.PV
UnivOut1_Object.SCPTovrBehave.PV

 

9 Universal Output 2 (%)
UnivOut2_Object.nviUnvOutput2.PV
UnivOut2_Object.nviUnvOutput2.SCPTovrValue.PV
UnivOut2_Object.SCPTovrBehave.PV

 

10 Universal Output 3 (%)
UnivOut3_Object.nviUnvOutput3.PV
UnivOut3_Object.nviUnvOutput3.SCPTovrValue.PV
UnivOut3_Object.SCPTovrBehave.PV
Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 4804
  • force
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of